Question

The operating temperature of a cold storage is - 2° C. The heat leakage from the surrounding is 30 kW for the ambient temperature of 40° C. The actual C.O.P. of refrigeration plant used is one fourth that of ideal plant working between the same temperatures. The power required to drive the plant is

a.

1.86 kW

b.

3.72 kW

c.

7.44 kW

d.

18.6 kW

Posted under Mechanical Engineering

Answer: (d).18.6 kW

Interact with the Community - Share Your Thoughts

Uncertain About the Answer? Seek Clarification Here.

Understand the Explanation? Include it Here.

Q. The operating temperature of a cold storage is - 2° C. The heat leakage from the surrounding is 30 kW for the ambient temperature of 40° C. The actual C.O.P. of refrigeration plant...

Similar Questions

Explore Relevant Multiple Choice Questions (MCQs)

Q. In chemical dehumidification process,

Q. A one tonne refrigerating machine means that

Q. The air cooling system mostly used in transport type aircrafts is

Q. The critical thickness of insulation is the ratio of thermal conductivity of the insulating material (k) to the heat transfer coefficient at the outer surface of the insulation (h0).

Q. The heat transfer by conduction through a thick cylinder(Q) is given by (where T1 = Higher temperature, T2 = Lower temperature, r1 = Inside radius, r2 = Outside radius, l = Length of cylinder, and k = Thermal conductivity)

Q. The heat is transferred by conduction, convection and radiation in

Q. A thermostatic expansion valve in a refrigeration system

Q. The temperature rise, between the condenser outlet and expansion valve in ammonia vapour compression system, should be as low as possible.

Q. The ratio of the actual mass of water vapour in a unit mass of dry air to the mass of water vapour in the same mass of dry air when it is saturated at the same temperature and pressure, is called

Q. The __________ point of ammonia is -77.7°C.

Q. Sulphur dioxide has the lowest boiling point.

Q. For a given dry bulb temperature, as the relative humidity __________ the wet bulb temperature will increase.

Q. The lowest thermal diffusivity is of

Q. A low wet bulb temperature indicates very __________ humidity.

Q. In counter-current flow heat exchanger, the logarithmic temperature difference between the fluids is __________ as compared to parallel flow heat exchanger.

Q. Environmental protection agencies advice against the use of chloro-fluoro-carbon refrigerants since

Q. When the lower temperature of a refrigerating machine is fixed, then the coefficient of performance can be improved by

Q. The refrigerant carbon dioxide is not widely used because of its __________ power require ments per tonne of refrigeration and high operating pressures.

Q. The by-pass factor of a cooling coil decreases with

Q. For unsaturated air, the dew point temperature is __________ wet bulb temperature.

Recommended Subjects

Are you eager to expand your knowledge beyond Mechanical Engineering? We've handpicked a range of related categories that you might find intriguing.

Click on the categories below to discover a wealth of MCQs and enrich your understanding of various subjects. Happy exploring!